Owen Duffy wrote in
: .... But, firstly, you should determine if there are regulatory requirements, such as NEC etc. Is "NFPA 780: Standard for the Installation of Lightning Protection Systems" a relevant standard in your jurisdiction? Owen |
#3
![]() |
|||
|
|||
![]()
Owen Duffy wrote in news:Xns9DB5277B6263Bnonenowhere@
61.9.134.55: .... Is "NFPA 780: Standard for the Installation of Lightning Protection Systems" a relevant standard in your jurisdiction? If it is applicable, it seems that for a Class 1 structure (less than 75' in height???), the requirement for the main down conductor is 57,400 circular mils CSA if copper, that is about 29mm^2 or #2 conductor. By contrast, #6 is 26,000 circular mils, has approximately twice the resistance per unit length, half the mass per unit length, and somewhere just less than 25% of the stroke current withstand of #2. Owen |
#4
![]() |
|||
|
|||
![]()
On Jul 13, 1:52*pm, Owen Duffy wrote:
Owen Duffy wrote : ... But, firstly, you should determine if there are regulatory requirements, such as NEC etc. Is "NFPA 780: Standard for the Installation of Lightning Protection Systems" a relevant standard in your jurisdiction? Owen Owen It is relevant as a consensus standard but it is not adopted as local or State law. Do you have a link to a copy that can be read online? -- Tom Horne, W3TDH |
#5
![]() |
|||
|
|||
![]()
Tom Horne wrote in
: .... Is "NFPA 780: Standard for the Installation of Lightning Protection Systems" a relevant standard in your jurisdiction? Owen Owen It is relevant as a consensus standard but it is not adopted as local or State law. Do you have a link to a copy that can be read online? Ok, well the question is whether you give it importance, or stay with NEC. I think it turns out that you have a copy, read it and make you own mind up. If it was me, I wouldn't waste the money on an inadequate protection scheme. Owen |
#6
![]() |
|||
|
|||
![]()
Tom Horne wrote:
On Jul 13, 1:52 pm, Owen Duffy wrote: Owen Duffy wrote : ... But, firstly, you should determine if there are regulatory requirements, such as NEC etc. Is "NFPA 780: Standard for the Installation of Lightning Protection Systems" a relevant standard in your jurisdiction? Owen Owen It is relevant as a consensus standard but it is not adopted as local or State law. Do you have a link to a copy that can be read online? NFPA 780, like NFPA 70, is a copyrighted document *sold* by NFPA. However, there *are* online copies of various provenance and age around. http://www.atmo.arizona.edu/students...A_780_2004.pdf Unfortunately, the bare code doesn't tell you much about the "why" for various code provisions, so if you're thinking of going "off code" for one reason or another, you don't have a lot of information to tell you whether it's a good idea. There's also some interesting seeming inconsistencies.. NFPA 780 requires a minimum length of a ground rod of 8 feet (4.13.2.1) but also requires that they extend vertically not less than 10 feet into the earth (4.13.2.3(A))) The figure makes it clear.. the top of an 8 foot rod is 2 feet below the surface of the soil. NFPA 780 says 29 square millimeters for main conductors (6 mm in diameter or a strip that is 1.3mm thick x 22.3 mm wide).. That's AWG 6 roughly. There's also a great site by Carl Malamud: publicresource.org that has all the California Building Codes (including an older rev of the NEC) although it doesn't have NFPA 780 on it, as far as I know. |
#7
![]() |
|||
|
|||
![]()
On Jul 13, 2:18*am, Owen Duffy wrote:
Tom Horne wrote in news:e802f6fa-b0e1-471b-bf31- : Can anyone make a recommendation, based on actual training and experience, as to what width and thickness of copper strap would be ... In this part of the world, we have an Australian / New Zealand Standard (our version if you like of ANSI, BS etc) which explains the rationale behind lightning protection, a method of estimating the downcurrent for protection design purposes and a process for designing down conductors. Broadly, the scheme is that downconductors are designed to withstand a few donwstrokes in quick succession without melting the down conductor. If you work from a peak current of 20kA, it would lead to a down conductor in copper of at least 25mm^2 which is about #2 to you folk. I regularly see hams recommend much thinner down conductors, and can only assume that there is not regulatory guidance or requirement, and I wonder at the effectiveness of using #6 as often recommended, especially aluminium as is often the case. Note that reducing conductor size is a double whammy, you increase the resistance (so the power), and decrease the mass that has to be heated to melting point, and so the energy required. But, firstly, you should determine if there are regulatory requirements, such as NEC etc. The question of equipotential bonding conductors ought be dealt with in the same way, though that is not to imply that they will be the same size. Owen Owen Believe it or not the NEC only calls for number ten American Wire Gage (AWG) or 5.261 (mm)2 for protective grounding conductors. Bonding conductors between electrodes are only required to be number six AWG or 13.30 (mm)2. So leaving aside the bad joke that is the NEC requirements I'm trying to get some idea of what best practice might be. -- Tom Horne, W3TDH |
#8
![]() |
|||
|
|||
![]()
Tom Horne wrote:
Owen Believe it or not the NEC only calls for number ten American Wire Gage (AWG) or 5.261 (mm)2 for protective grounding conductors. Bonding conductors between electrodes are only required to be number six AWG or 13.30 (mm)2. So leaving aside the bad joke that is the NEC requirements I'm trying to get some idea of what best practice might be. Tom is a bit confused here about the purpose of NEC vs NFPA 780.. The bonding requirements in the NEC are designed to keep the building from burning down in the event of an accidental fault to an energized conductor. The basic requirement is that it carry enough fault current for long enough to trip the overcurrent protection device on the energized conductor. It's not for lightning protection, per se. (although NEC bonding will, incidentally, provide some degree of protection against induced transients) I'd also note that AWG 10 wire is more than sufficient to carry a 50kA pulse for the 20 microseconds or so that a lightning stroke lasts without melting. Using the Onderdonk equation, you can calculate that a AWG16 copper wire will carry about 90kA for a 20 microsecond pulse. AWG10 should be able to carry 4 times that much. AWG6, 10 times, because it scales with cross sectional area. Having only really paid attention to this recently, I noticed that in Rome (a place with a fair number of thunderstorms), they use fairly small down conductors (AWG 10 or 6, just by eye), and similar for 7 story tall wooden pagodas in Nara, Japan (another place with lots of thunderstorms). I'm not quite sure where the fashion for 2/0 grounding conductors comes from (maybe Phelps-Dodge has a representative on the NFPA 780 review committee?grin) |
#9
![]() |
|||
|
|||
![]()
On Jul 13, 2:18*am, Owen Duffy wrote:
Tom Horne wrote in news:e802f6fa-b0e1-471b-bf31- : Can anyone make a recommendation, based on actual training and experience, as to what width and thickness of copper strap would be ... In this part of the world, we have an Australian / New Zealand Standard (our version if you like of ANSI, BS etc) which explains the rationale behind lightning protection, a method of estimating the downcurrent for protection design purposes and a process for designing down conductors. Broadly, the scheme is that downconductors are designed to withstand a few donwstrokes in quick succession without melting the down conductor. If you work from a peak current of 20kA, it would lead to a down conductor in copper of at least 25mm^2 which is about #2 to you folk. I regularly see hams recommend much thinner down conductors, and can only assume that there is not regulatory guidance or requirement, and I wonder at the effectiveness of using #6 as often recommended, especially aluminium as is often the case. Note that reducing conductor size is a double whammy, you increase the resistance (so the power), and decrease the mass that has to be heated to melting point, and so the energy required. But, firstly, you should determine if there are regulatory requirements, such as NEC etc. The question of equipotential bonding conductors ought be dealt with in the same way, though that is not to imply that they will be the same size. Owen Owen The NEC only requires 5.261 (mm)2 for the protective down conductor and 13.30 (mm)2 for the bonding conductor between electrodes. Since those sizes are at best a bad joke I was hoping to elicit best practice advise on what size the conductors should actually be as well as advise on how to accomplish the bonding of the interior single point grounding buss bar to the exterior grounding conductors and Grounding Electrode System. -- Tom Horne, W3TDH |
#10
![]() |
|||
|
|||
![]()
On Jul 15, 9:18*pm, Tom Horne wrote:
Owen The NEC only requires 5.261 (mm)2 for the protective down conductor and 13.30 (mm)2 for the bonding conductor between electrodes. *Since those sizes are at best a bad joke I was hoping to elicit best practice advise on what size the conductors should actually be as well as advise on how to accomplish the bonding of the interior single point grounding buss bar to the exterior grounding conductors and Grounding Electrode System. -- Tom Horne, W3TDH It's not that bad a joke.. If the ground connection is good, #10 is plenty thick enough. In fact, it would barely get warm if it took a strike. Of course, if the connection to ground is bad, it will be toast. But so would a lot of heavier gauges also.. The connection to ground is the critical factor in such a case. But I would still follow what the local code says. The main reason I'm making this post is only to clarify that under proper conditions, #10 is plenty thick enough to safely route the strike to ground with no damage to the wire. |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
FS CDE Lower Mast Mounting Bracket | Swap | |||
FS CDE Lower Mast Mounting Bracket | Boatanchors | |||
FS CDE Lower Mast Mounting Bracket | Equipment | |||
Roof Mounting bracket For Rohn HD-70 Mast? | Antenna | |||
telescopic mast mounting bracket | CB |