ku4yp wrote:
i have a question. in reference to station grounding, i have read keep the grounding strap as short as possible and not a multiple of a resonant length on the ham bands. with that in mind, even if i ground pieces of equipment to individual ground rods, won't the complete grounding system be long? in my mind i am looking around the room and seeing a grounding system being at least 12 feet long, if i go along the perimeter of the desks (which are in a "U" shape in the room. W1MCE replies: I have used a 1/2 inch copper pipe mounted along the back edge of the table[s] holding my station equipment. The case of each piece of equipment is connected directly to the copper pipe using 1 inch braided strap about 6 to 12 inches long depending on equipment size. This pipe provides an equipotential plane for all my equipment. [Another method would be to install a thin copper sheath on top of your desk/tables and connect directly to it for the equipotential plane.] Now, how to connect the equipotential plane to brown dirt [earth] is the next issue. You are correct that it is desirable to keep this 'non-resonant' on the bands you operate. There are two issues here that need to be addressed. First, if you are close to the earth ground then a simple #6 AWG wire to a ground rod is adequate. Second, if you are higher than 1/4 wavelength at the highest frequency of interest use two #6 AWG wires OF DIFFERENT LENGTHS, not harmonically related, connected to the ground rod. The different lengths assure that the equivalent connection is NOT RESONANT. In very fortunate cases an additional station ground is not required! Believe it or not! ... My station is located on the ground floor in the family [my] TV room right under the electrical distribution panel. My 120 VAC line comes directly from the service entrance through about 3 feet of wire. The 240 VAC for my amplifier comes directly from the service entrance through 4 feet of wire. The service box is 'earthed' by a NEC compliant connection. My connections to the service box are therefore very short. A major point of caution is required. The NEC requires ONLY ONE ground connection. Multiple ground connections introduce VERY SERIOUS ground loops that may violate the NEC criteria. This opens a VERY LARGE loop hole in your home owner's insurance policy. If you are adding a second earth [ground] connection at your station use an isolation transformer to break up the ground loops in the basic 120 VAC connection. Consult with an electrician regarding your local and NEC codes. It is noted that station grounding and antenna counterpoise construction are two different things. I am not addressing the counterpoise issue. |
#2
|
|||
|
|||
Dave Shrader wrote:
. . . A major point of caution is required. The NEC requires ONLY ONE ground connection. Multiple ground connections introduce VERY SERIOUS ground loops that may violate the NEC criteria. This opens a VERY LARGE loop hole in your home owner's insurance policy. If you are adding a second earth [ground] connection at your station use an isolation transformer to break up the ground loops in the basic 120 VAC connection. Consult with an electrician regarding your local and NEC codes. . . . My NEC book is getting pretty old now, 1990, but at that time, multiple grounds were often not only permitted, but required. And a *minimum* spacing was sometimes specified. For example, section 250-84, Resistance of Made Electrodes: "A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified in Sections 250-81 or 250-83. Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall be not less than 6 feet (1.83m) apart." Or section 250-81(a), Metal Underground Water Pipe: ". . .A metal underground water pipe shall be supplemented by an additional electrode of a type specified in Section 250-81 or in Section 250-83. The supplemental electrode shall be permitted to be bonded to the grounding electrode conductor, the grounded service-entrance conductor, the grounded service raceway, any grounded sevice enclosure, or the interior metal water piping at any convenient point." When I replaced the service (in 1979) in my 1952 house, the system ground was a water pipe connection and I was required to add a ground rod. Neither was considered adequate in itself; both were required by the code at that time. I agree wholeheartedly about consulting an electrician. Non-electricians (including me) often have mistaken ideas about the content of the NEC. It doesn't hurt to have an up to date copy of the NEC for reference, either, if you anticipate doing any of the work yourself. Roy Lewallen, W7EL |
#3
|
|||
|
|||
"Roy Lewallen" wrote Dave Shrader wrote: . . . A major point of caution is required. The NEC requires ONLY ONE ground connection. Multiple ground connections introduce VERY SERIOUS ground loops that may violate the NEC criteria. This opens a VERY LARGE loop hole in your home owner's insurance policy. If you are adding a second earth [ground] connection at your station use an isolation transformer to break up the ground loops in the basic 120 VAC connection. Consult with an electrician regarding your local and NEC codes. . . . My NEC book is getting pretty old now, 1990, but at that time, multiple grounds were often not only permitted, but required. And a *minimum* spacing was sometimes specified. Outdated only regarding water pipe Roy, but good advice. And Dave's above interpretation of NEC is a misunderstanding of the subject - easy to do so consult a professional if you have any douvbt whatsoever about what your are doing. Isolation transformers are not an option for isolating a station ground from AC service entrance. They are permitted only in lmited cases where independent grounding is required, and in other cases where HV isolating transformers or fiber optic isolate feedlines. No one in this group will likely have that requirement, so put that out of your mind Dave. You *MUST* bond your station ground to the AC service main ground. Ignore this at the peril of your entire system, which had better be 100% isolated from all power and external feedlines and grounds. That is an option for protection, isolating from *everything*. But it means unplugging and shorting to ground all feedlines, disconnecting and removing RF ground connections, disconnecting computer modems, telephone, and AC power to all of your connected equipment. A really poor option in my opinion, because if you forget something, or risk your life trying to disconnect during a surprise thunderstorm, what was it worth? For example, section 250-84, Resistance of Made Electrodes: "A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified in Sections 250-81 or 250-83. Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall be not less than 6 feet (1.83m) apart." Or section 250-81(a), Metal Underground Water Pipe: ". . .A metal underground water pipe shall be supplemented by an additional electrode of a type specified in Section 250-81 or in Section 250-83. The supplemental electrode shall be permitted to be bonded to the grounding electrode conductor, the grounded service-entrance conductor, the grounded service raceway, any grounded sevice enclosure, or the interior metal water piping at any convenient point." When I replaced the service (in 1979) in my 1952 house, the system ground was a water pipe connection and I was required to add a ground rod. Neither was considered adequate in itself; both were required by the code at that time. I agree wholeheartedly about consulting an electrician. Non-electricians (including me) often have mistaken ideas about the content of the NEC. It doesn't hurt to have an up to date copy of the NEC for reference, either, if you anticipate doing any of the work yourself. Roy Lewallen, W7EL Jack Painter Virginia Beach VA |
#4
|
|||
|
|||
Roy Lewallen wrote:
Dave Shrader wrote: . . . A major point of caution is required. The NEC requires ONLY ONE ground connection. Multiple ground connections introduce VERY SERIOUS ground loops that may violate the NEC criteria. This opens a VERY LARGE loop hole in your home owner's insurance policy. If you are adding a second earth [ground] connection at your station use an isolation transformer to break up the ground loops in the basic 120 VAC connection. Consult with an electrician regarding your local and NEC codes. . . . My NEC book is getting pretty old now, 1990, but at that time, multiple grounds were often not only permitted, but required. And a *minimum* spacing was sometimes specified. For example, section 250-84, Resistance of Made Electrodes: "A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified in Sections 250-81 or 250-83. Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall be not less than 6 (1.83m) apart." Is it something like this? Multiple ground rods are permitted (encouraged, even) in order to establish one good ground connection; but the wiring system can have only one ground connection. -- 73 from Ian G3SEK 'In Practice' columnist for RadCom (RSGB) http://www.ifwtech.co.uk/g3sek |
#5
|
|||
|
|||
Ian White, G3SEK wrote: Roy Lewallen wrote: My NEC book is getting pretty old now, 1990, but at that time, multiple grounds were often not only permitted, but required. And a *minimum* spacing was sometimes specified. For example, section 250-84, Resistance of Made Electrodes: "A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified in Sections 250-81 or 250-83. Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall be not less than 6 (1.83m) apart." Is it something like this? Multiple ground rods are permitted (encouraged, even) in order to establish one good ground connection; but the wiring system can have only one ground connection. Well, yes and no. As I read it, all the ground electrodes have to be connected to the service box, as they are at my house. I have a water-pipe ground and a ground rod; they're physically widely separated, and each has its own conductor going back to the service box. So I guess you could call the service box a single "ground connection". The neutral and safety ground conductors of each circuit are individually grounded at the service box also, giving further support to interpreting its function as a single ground connection. A number of ground methods and devices are approved, such as buried rods or plates, concrete grounds, or (in my old code book anyway), water pipe ground. Some can be used alone and others need a second ground device as a supplement. When multiple ground rods are used, the code has requirements for bonding them to each other. Roy Lewallen, W7EL |
#6
|
|||
|
|||
"Roy Lewallen" wrote in message ... Ian White, G3SEK wrote: Roy Lewallen wrote: My NEC book is getting pretty old now, 1990, but at that time, multiple grounds were often not only permitted, but required. And a *minimum* spacing was sometimes specified. For example, section 250-84, Resistance of Made Electrodes: "A single electrode consisting of a rod, pipe, or plate which does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified in Sections 250-81 or 250-83. Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall be not less than 6 (1.83m) apart." Is it something like this? Multiple ground rods are permitted (encouraged, even) in order to establish one good ground connection; but the wiring system can have only one ground connection. Well, yes and no. As I read it, all the ground electrodes have to be connected to the service box, as they are at my house. I have a water-pipe ground and a ground rod; they're physically widely separated, and each has its own conductor going back to the service box. So I guess you could call the service box a single "ground connection". The neutral and safety ground conductors of each circuit are individually grounded at the service box also, giving further support to interpreting its function as a single ground connection. A number of ground methods and devices are approved, such as buried rods or plates, concrete grounds, or (in my old code book anyway), water pipe ground. Some can be used alone and others need a second ground device as a supplement. When multiple ground rods are used, the code has requirements for bonding them to each other. Roy Lewallen, W7EL Using a cold water pipe is a bad idea and is not allowed by some local codes even though it may be allowed by the national code. This is partly because it should only be connected to the ground system at one point and it is too easy to connect it at more than one. Also there is the possible interaction with gas lines and plumbers and home owners sometimes modify plumbing in ways that make them poor grounds.. |
#7
|
|||
|
|||
Jimmy wrote:
"Using a cold water pipe is a bad idea and is not allowed by some local codes even though it may be allowed by the national code." You don`t want to be electrocuted when holding an electric appliance and a cold water valve simultaneously. My electric company, the former Houston Lighting and Power Company, writes: "All services shall be properly grounded. Note - NEC requires grounding to a "metallic underground water piping system" if available. Acceptable alternatives include a driven ground rod which is preferred by HL&P Co. regardless of the type grounding electrode used. NEC requires that the "interior cold water pipimg system" be bonded to it." Best regards, Richard Harrison, KB5WZI |
#8
|
|||
|
|||
Richard Harrison wrote:
My electric company, the former Houston Lighting and Power Company, writes: "All services shall be properly grounded. Note - NEC requires grounding to a "metallic underground water piping system" if available. Acceptable alternatives include a driven ground rod which is preferred by HL&P Co. regardless of the type grounding electrode used. NEC requires that the "interior cold water pipimg system" be bonded to it." That last point is the same in the UK. Gas and water supplies are never relied on to provide an electrical ground, but they must be bonded to the electrical supply ground. Additional local bonding is also required for all metalwork in bathrooms and shower rooms. -- 73 from Ian G3SEK 'In Practice' columnist for RadCom (RSGB) http://www.ifwtech.co.uk/g3sek |
#9
|
|||
|
|||
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
CD Player Receives FM Station | Antenna | |||
Newbie - Studying for Tech & planning station setup - Vertical antennaquestion | Antenna | |||
Antenna mast grounding question | Antenna | |||
Grounding for Vertical Question | Antenna | |||
Grounding question - this is wierd..... | Antenna |