			ku4yp wrote:i have a question.
 
 in reference to station grounding, i have read keep the grounding strap
 as short as possible and not a multiple of a resonant length on the ham
 bands. with that in mind, even if i ground pieces of equipment to individual
 ground rods, won't the complete grounding system be long? in my mind i am
 looking around the room and seeing a grounding system being at least 12 feet
 long, if i go along the perimeter of the desks (which are in a "U" shape in
 the room.
 
 W1MCE replies:
 
 I have used a 1/2 inch copper pipe mounted along the back edge of the
 table[s] holding my station equipment.
 
 The case of each piece of equipment is connected directly to the copper
 pipe using 1 inch braided strap about 6 to 12 inches long depending on
 equipment size. This pipe provides an equipotential plane for all my
 equipment. [Another method would be to install a thin copper sheath on
 top of your desk/tables and connect directly to it for the equipotential
 plane.]
 
 Now, how to connect the equipotential plane to brown dirt [earth] is the
 next issue. You are correct that it is desirable to keep this
 'non-resonant' on the bands you operate. There are two issues here that
 need to be addressed. First, if you are close to the earth ground then a
 simple #6 AWG wire to a ground rod is adequate. Second, if you are
 higher than 1/4 wavelength at the highest frequency of interest use two
 #6 AWG wires OF DIFFERENT LENGTHS, not harmonically related, connected
 to the ground rod. The different lengths assure that the equivalent
 connection is NOT RESONANT.
 
 In very fortunate cases an additional station ground is not required!
 Believe it or not! ... My station is located on the ground floor in the
 family [my] TV room right under the electrical distribution panel. My
 120 VAC line comes directly from the service entrance through about 3
 feet of wire. The 240 VAC for my amplifier comes directly from the
 service entrance through 4 feet of wire. The service box is 'earthed' by
 a NEC compliant connection. My connections to the service box are
 therefore very short.
 
 A major point of caution is required. The NEC requires ONLY ONE ground
 connection. Multiple ground connections introduce VERY SERIOUS ground
 loops that may violate the NEC criteria. This opens a VERY LARGE loop
 hole in your home owner's insurance policy.  If you are adding a second
 earth [ground] connection at your station use an isolation transformer
 to break up the ground loops in the basic 120 VAC connection. Consult
 with an electrician regarding your local and NEC codes.
 
 It is noted that station grounding and antenna counterpoise construction
 are two different things. I am not addressing the counterpoise issue.
 
 
 |