Home |
Search |
Today's Posts |
|
#1
![]() |
|||
|
|||
![]() Owen The fusing/melting current for 1/2" copper pipe is probably well above 20kA, even for 100ms pulses. A more interesting potential failure mode might be from the mechanical forces due to the magnetic field. (see, e.g., quarter shrinking or can-crushing) Hi Jim, I note the "probably" in your comment, and the "dunno" in N5MK's response. That's because I was lazy and didn't want to actually compute it. I've put multi tens of kA pulses through 1/4" copper pipe, but they're not 100ms long. The uncertainty in my statement is over the exact lightning scenario, they vary, and the circuit response (ie current waveshape, amplitude, duration, ringing etc) depend on the specific excitation and circuit elements (parameters of the down conductor, nature of the earth system, ground, environment etc). One could certainly use the standard double exponential approximations.. either a 2/50 waveform for a strike or the longer surge impulse (I can't remember the exact rise/fall times for the surge..) As far as supposition as to the fusing current for conductors, that is determinable for a given scenario. I have at hand the Protective Earthing Code of Practice published by the Electricity Authority of NSW June 1975 and it shows that a 35mm^2 copper conductor has a fault current withstand of 20kA for 100ms. (I have considered implementing the underlying formulas in an online calculator.) Preece or Onderdonk? (http://home.earthlink.net/~jimlux/hv/fuses.htm N5MK stated "A #10 wire can handle that job". If he is talking copper, I understand that #10 means 2.5mm diameter, or ~5mm^2, or less than 15% of the recommended conductor csa for the stated scenario. Preece equation gives fusing current for AWG10 (2.5mm diameter, as you say) as 316 amps, but that's sort of for a steady state. Onderdonk's equation, plugging in 100 ms for the melt time, gives 4.7kA, which I can believe. I've blown up a lot of AWG10 wire with those sorts of currents in a quarter shrinker. Partly melting, partly mechanical stresses in that application. The purpose of the National Electrical Code (National, here, referring chauvinistically to the U.S.) required AWG 6 (diam 0.15 inches, 3.8 mm) bonding wire for grounds is NOT to carry the lightning current (which it wouldn't, in most cases) but to carry fault currents from things like shorts from line to grounding conductor, which are usually in the hundreds of amps range. Say an energized power line falls down and hits the antenna. You want the antenna's grounding conductor to carry the likely fault current and not go open, and carry enough current to trip any overcurrent protective devices. Lightning protection is usually things like 2/0 (0.364 inch diameter, 9.25 mm), which has a fusing current (viz Onderdonk) of 65kA. I am not familiar with your water pipe sizes. If it were, say, a half inch diameter #19, it has a CSA of around 35mm^2, so the #10 wire should melt before the pipe electrode, thus protecting the pipe electrode from failure. Yes, mechanical forces are also relevant to lightning conductors, but my comment was about the fusing current. 35 mm^2 would have a fusing current of around 30-35 kA. 1/2" Copper pipe is 0.625" od and 0.545" id (very close to 1mm wall) so, has about 47 mm^2 area. In this part of the world there is an Australian Standard (AS1768) relating to lightning protection, there may be a similar standard or "code" in other jurisdictions, and they would not be a bad place to start in understanding lightning protection and designing a protection scheme. Another source of information is to walk around a mobile phone base station and look at the earthing system from the outside. It is even more enlightning (no pun) to look inside. These things withstand lightning events quite well. Are they over engineered? Probably not, they do suffer damage from time to time. It is my view that there is a significant risk that an inadequate lightning protection scheme may be much worse than doing nothing. I would agree.. Owen |
#2
![]() |
|||
|
|||
![]()
....
Jim, a lot of interesting stuff with which I generally agree. The approach that my reference took to rating the conductor for a lightning discharge includes a safety factor (as you might expect), and so will rate the conductor at lower I^2*t than finding the conditions to melt the wire. In real life, you would want the conductor to withstand a second strike or fault soon after, and you would want to allow some tolerance for other variables, hence the safety factor. The approach is to find the I^2*t that raises the conductor one third of the way from ambient (323K) to melting point. The calculator you used might assume resistivity is at 0°C , ambient is 0°C, and the material is raised to melting point with no heat loss, and that would give a fusing current close to double of the approach that I used. BTW, we have half inch copper water pipe over here (we still do but it has a nominal metric size) and it is half in od... whereas half inch galvanised steel pipe is half inch nominal bore... actually about 5/8" id. Don't you like consistency in the same field! Some years ago I did extensive modelling of a double exponential excitation of structures and facilities (not lightning, faster than lightning) and it was interesting how much the circuit configuration affected the transformation of the excitation waveform to structure current, including ringing. The same software could run a lightning scenario, but that wasn't the main goal of the analysis so my experience with the lightning scenario is more limited. So, as I said, the nature of the current waveform is the big uncertainty and so measures are usually quite conservative to cover that uncertainty. Owen |
#3
![]() |
|||
|
|||
![]()
Owen Duffy wrote:
... Jim, a lot of interesting stuff with which I generally agree. The approach that my reference took to rating the conductor for a lightning discharge includes a safety factor (as you might expect), and so will rate the conductor at lower I^2*t than finding the conditions to melt the wire. In real life, you would want the conductor to withstand a second strike or fault soon after, and you would want to allow some tolerance for other variables, hence the safety factor. The approach is to find the I^2*t that raises the conductor one third of the way from ambient (323K) to melting point. The calculator you used might assume resistivity is at 0°C , ambient is 0°C, and the material is raised to melting point with no heat loss, and that would give a fusing current close to double of the approach that I used. BTW, we have half inch copper water pipe over here (we still do but it has a nominal metric size) and it is half in od... whereas half inch galvanised steel pipe is half inch nominal bore... actually about 5/8" id. Don't you like consistency in the same field! But they're not the same field.. the stuff made of copper is actually "tubing" and the stuff made of steel is "pipe", and historically, they've been measured differently. Tubing is usually soldered/sweated/brazed into fittings with a receptacle, so the OD is important, because even with different wall thicknesses, the fittings are all the same. Pipe is based on something else (King John's toe diameter or something) Some years ago I did extensive modelling of a double exponential excitation of structures and facilities (not lightning, faster than lightning) and it was interesting how much the circuit configuration affected the transformation of the excitation waveform to structure current, including ringing. The same software could run a lightning scenario, but that wasn't the main goal of the analysis so my experience with the lightning scenario is more limited. So, as I said, the nature of the current waveform is the big uncertainty and so measures are usually quite conservative to cover that uncertainty. There's some fascinating papers out there that use NEC to model response to a nearby lightning stroke (a much more common occurance than a direct hit). It's actually quite involved, since they model the traveling impulse of the stroke. Owen |
#4
![]() |
|||
|
|||
![]() We had a near by lightning strike last night... All my radios and antennas survived... My son's Dish Network receiver did not... He's quite bummed out... denny |
#5
![]() |
|||
|
|||
![]()
Jim Lux wrote in
: The purpose of the National Electrical Code (National, here, referring chauvinistically to the U.S.) required AWG 6 (diam 0.15 inches, 3.8 mm) bonding wire for grounds is NOT to carry the lightning current (which it wouldn't, in most cases) but to carry fault currents from things like shorts from line to grounding conductor, which are usually in the hundreds of amps range. Say an energized power line falls down and hits the antenna. You want the antenna's grounding conductor to carry the likely fault current and not go open, and carry enough current to trip any overcurrent protective devices. I meant to comment: I think that it is common in electricity distribution level networks, that they are designed to hold fault current to about 20 times the maximum working current. In this part of the world, a single phase 240 home probably has a 80A rated service, and fault current would usually be not worse than than about 1600A, so the specified 6mm^2 earthing conductor and 4mm^2 bonding conductor should withstand that current for 100ms until the protective device operates. (4mm^2 withstands 3200A for 0.1s with a safety factor of 3.) You probably know the numbers for your own distribution network practice, they may be of interest to readers. So you raise a good point, that if your tower falls onto power lines, it would be good if your earth system could withstand the likely fault current to take out the protection on the power lines and leave the tower un-energised. In this part of the world with LV distribution, the protection is probably a 500A HRC fuse with a fault current level of 10 +kA. It may be much lower for you if power lines are HV where the fault current level should be a good deal lower. Owen |
#6
![]() |
|||
|
|||
![]()
Owen Duffy wrote in
: protective device operates. (4mm^2 withstands 3200A for 0.1s with a safety factor of 3.) That should read: protective device operates. (4mm^2 withstands 2400A for 0.1s with a safety factor of 3.) |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Building a Solid Copper Ground Pipe {Tube} with an Solid Iron Core. - Also - Water Drilling a Solid Copper Pipe for a Ground Rod. | Shortwave | |||
Building a Solid Copper Ground Pipe {Tube} with an Solid IronC... | Shortwave | |||
Cold Water Pipe Ground? | Antenna | |||
Ground rod or water pipe? | Antenna | |||
Antenna Tuner/Coupler Ground ... Hot Water Pipe? | Antenna |