Jimmie wrote:
Should re read what I write sometimes. I was refering to using the water pipe as the sole ground for your electrical system. This used to be a common thing and pemissable by the NEC, not sure if it still is. When I replaced my service in 1975, a water pipe ground (which is all my 1952 house had) wasn't sufficient to satisfy the NEC, so I had to add a ground rod. So the NEC hasn't permitted a water pipe ground as the sole ground for at least 29 years. It apparently was permissible in 1952. Roy Lewallen, W7EL |
#3
![]() |
|||
|
|||
![]()
So the NEC hasn't permitted a water pipe ground as the sole
ground for at least 29 years. Roy Lewallen, W7EL ===================================== A good thing too. At any time a fully qualified plumber can come along and replace a section of metal water pipe with polyethelene, one of the best insulating materials known to science. |
#4
![]() |
|||
|
|||
![]()
I am not very familiar with USA power-grounding regulations and they
probably vary from state to state. But I am under the impression that in some simple circumstances, perhaps domestic, a single ground rod is considered adequate for safety purposes. Under similar circumstances a maximum ground electrode resistance ( whatever its construction ) of 50 ohms is specified. A 'standard' ground rod is 8 feet long and 1 inch in diameter. An average soil resistivity is 500 ohm-metres ( = 2 mS ). See Eznec? The calculated resistance of a single standard rod in average soil is 194 ohms. ( I'm sure the calculating formula can be found somewhere on the IEEE shelves. There ought to be greater use made of it. ) Now I don't expect the alarm bells to be rung from Washington to LA. But isn't there a serious inconsistency somewhere? As a matter of interest, the resistances to ground of 2, 3 and 4 rods in parallel, spaced 6 feet apart in average soil, are as follows - 2 Rods = 113 ohms 3 Rods = 86 ohms 4 Rods = 70 ohms all of which exceed the specified maximum of 50 ohms. Quite a low average soil resistivity of about 130 ohms is needed to bring 50 percent of installations within specification. If my starting data is wildly adrift then disregard my waffle. ---- Reg, G4FGQ |
#5
![]() |
|||
|
|||
![]()
yeah, and its worse than that. most times they only use 1/2" or 5/8"
diameter rods, and the 6' spacing becomes 3' 'or so' when they do more than one, which seems to be getting more common. the last electrician i hired actually put 2 rods at a separate garage service entrance without being prompted.... but maybe it was all the towers and other rods around that convinced him he should do it right before i said anything. "Reg Edwards" wrote in message ... I am not very familiar with USA power-grounding regulations and they probably vary from state to state. But I am under the impression that in some simple circumstances, perhaps domestic, a single ground rod is considered adequate for safety purposes. Under similar circumstances a maximum ground electrode resistance ( whatever its construction ) of 50 ohms is specified. A 'standard' ground rod is 8 feet long and 1 inch in diameter. An average soil resistivity is 500 ohm-metres ( = 2 mS ). See Eznec? The calculated resistance of a single standard rod in average soil is 194 ohms. ( I'm sure the calculating formula can be found somewhere on the IEEE shelves. There ought to be greater use made of it. ) Now I don't expect the alarm bells to be rung from Washington to LA. But isn't there a serious inconsistency somewhere? As a matter of interest, the resistances to ground of 2, 3 and 4 rods in parallel, spaced 6 feet apart in average soil, are as follows - 2 Rods = 113 ohms 3 Rods = 86 ohms 4 Rods = 70 ohms all of which exceed the specified maximum of 50 ohms. Quite a low average soil resistivity of about 130 ohms is needed to bring 50 percent of installations within specification. If my starting data is wildly adrift then disregard my waffle. ---- Reg, G4FGQ |
#6
![]() |
|||
|
|||
![]() "Reg Edwards" wrote I am not very familiar with USA power-grounding regulations and they probably vary from state to state. But I am under the impression that in some simple circumstances, perhaps domestic, a single ground rod is considered adequate for safety purposes. Under similar circumstances a maximum ground electrode resistance ( whatever its construction ) of 50 ohms is specified. A 'standard' ground rod is 8 feet long and 1 inch in diameter. An average soil resistivity is 500 ohm-metres ( = 2 mS ). See Eznec? The calculated resistance of a single standard rod in average soil is 194 ohms. ( I'm sure the calculating formula can be found somewhere on the IEEE shelves. There ought to be greater use made of it. ) Now I don't expect the alarm bells to be rung from Washington to LA. But isn't there a serious inconsistency somewhere? As a matter of interest, the resistances to ground of 2, 3 and 4 rods in parallel, spaced 6 feet apart in average soil, are as follows - 2 Rods = 113 ohms 3 Rods = 86 ohms 4 Rods = 70 ohms all of which exceed the specified maximum of 50 ohms. Quite a low average soil resistivity of about 130 ohms is needed to bring 50 percent of installations within specification. If my starting data is wildly adrift then disregard my waffle. ---- Reg, G4FGQ Yes Reg, sorry the figures are (thankfully) in error. Especially since 25ohm is required by our U.S. NEC, and that's easily attained in some soils, not so easy in others. This is being changed in the 2004 code changes, but it was paraphrased below: The NEC does not specify a maximum earth resistance for the grounding electrode system required under Article 250-81. The only place that does specify earth resistance is under Article 250-84, for "made" (rod, pipe, and plate) electrodes. Here the NEC specifies a resistance to ground of 25 Ohms or less for a single electrode. If the electrode does not meet 25 Ohms, it must be supplemented by one additional electrode. However the combination of the two electrodes does not have to meet the 25 ohm requirement! http://www.cpccorp.com/deep.htm Neither should anyone be overly concerned with acheiving low DC-resistivity of a grounded electrode. In spite of some interesting comments about their perceived successes in the white paper I cited above, the grounding issue is usually overstated - the ground for lightning is the real issue, as any 10' 5/8" copper rod earth ground works for 60hz electrical safety. For safe termination of lightning downconductors and mast grounds etc, the best ground you can reasonably achieve is going to be enough - as long as the principles of bonding are adhered to religiously. That means as close to equipotential as possible, and it does not assume a good ground, or even any ground at all in certain cases. We surely want the best ground reasonably attainable, and if you can sink 30' of connected rods, great. If you sink a few 8-foot 5/8" or a couple of 1"x10', even better. See the data in that paper above for some sample resistance measurements which they consider "average" (ha - Richard Clark's laughing ;-), rightfully so. Best regards, Jack |
#7
![]() |
|||
|
|||
![]()
On Thu, 9 Sep 2004 23:45:44 -0400, "Jack Painter"
wrote: http://www.cpccorp.com/deep.htm See the data in that paper above for some sample resistance measurements which they consider "average" Hi Jack, Interesting link. The paper offered was a model of terse reporting, sticking only with the facts as best they could come by them, and little in the way of overextending themselves with fanciful interpretations. The averages were what they found for themselves, not abstracted and generalized to the world at large. I would suggest that they also made some cogent observations about the soil structure that goes beyond myths and software passing as the new age equivalent of old wive's tales. I would further observe that making a declaration of what the resistance of ONE electrode is, is farcical in the extreme. It would take two to tango and with that second one added to measure the first, problems abound! Especially notable is the 10 fold variation in reported electrode resistance over a 4 year period, and the 10 fold variation of electrode resistance within a survey group. Such an error range easily eclipses what is taken on faith as "average ground." And then we have to ask ourselves that embarrassing question, just how does the mud in my backyard compare to "average?" Your comments on That means as close to equipotential as possible, and it does not assume a good ground, or even any ground at all in certain cases. translate with fungible results to RF for the same reason. No one here knows what quality ground they live over (really! to one skin depth at HF?). I would still like to know how many radials Reggie needs for his several KOhm mud in his garden. No, I take that back, what I want to know is what parameters he puts into the software that predicts the number of radials - and why would it matter? 73's Richard Clark, KB7QHC |
#8
![]() |
|||
|
|||
![]() "Richard Clark" wrote in message ... On Thu, 9 Sep 2004 23:45:44 -0400, "Jack Painter" wrote: http://www.cpccorp.com/deep.htm See the data in that paper above for some sample resistance measurements which they consider "average" Hi Jack, Interesting link. The paper offered was a model of terse reporting, sticking only with the facts as best they could come by them, and little in the way of overextending themselves with fanciful interpretations. The averages were what they found for themselves, not abstracted and generalized to the world at large. I would suggest that they also made some cogent observations about the soil structure that goes beyond myths and software passing as the new age equivalent of old wive's tales. I would further observe that making a declaration of what the resistance of ONE electrode is, is farcical in the extreme. It would take two to tango and with that second one added to measure the first, problems abound! Especially notable is the 10 fold variation in reported electrode resistance over a 4 year period, and the 10 fold variation of electrode resistance within a survey group. Such an error range easily eclipses what is taken on faith as "average ground." And then we have to ask ourselves that embarrassing question, just how does the mud in my backyard compare to "average?" Your comments on That means as close to equipotential as possible, and it does not assume a good ground, or even any ground at all in certain cases. translate with fungible results to RF for the same reason. No one here knows what quality ground they live over (really! to one skin depth at HF?). I would still like to know how many radials Reggie needs for his several KOhm mud in his garden. No, I take that back, what I want to know is what parameters he puts into the software that predicts the number of radials - and why would it matter? they 'why' is the real question as there are several reasons to design a 'ground' and each of them has different requirements. a few examples with different needs: 1. home electrical safety ground. 2. electrical substation ground. 3. hv transmission line ground for step or touch potential. 4. hv transmission line ground for lightning protection. 5. building ground for lightning protection. 6. building ground for rf isolation 7. vertical antenna ground for rf return these are all very different problems requiring very different solutions. i write software, part of which helps design grounds for hv transmission line structures. the theory and practice in this area is quite different from that used to design any of the other types (except maybe for small buildings requiring lightning protection). And some of the extensive testing we have done on the physics of the problem shows that the ground reacts quite differently from what most people expect when trying to dissipate lightning transients. i wouldn't use my software to design a ground for my station, though i did use some of the results of our tests to convince myself that what i did do would be adequate. Nor would i take any one other program as gospel when designing a ground for any particular type of installation. indeed at my station i have several different types of 'ground' systems, raised radials under elevated verticals, wire mesh mats on the ground under elevated verticals, ground rods at towers and service entrances, ufer grounds in foundations, perimeter ground around the house, each for a slightly different purpose and no one good enough for all the jobs that need to be done. Some help with rf radiation from antennas, some are lightning protection, and some are for ac safety. and they can't be interchanged in most cases... and some of them would not fit most layman's definition of what a 'ground' even is. |
#9
![]() |
|||
|
|||
![]()
On Thu, 9 Sep 2004 22:16:35 +0000 (UTC), "Reg Edwards"
wrote: |I am not very familiar with USA power-grounding regulations and they |probably vary from state to state. But I am under the impression that in |some simple circumstances, perhaps domestic, a single ground rod is |considered adequate for safety purposes. | |Under similar circumstances a maximum ground electrode resistance ( whatever |its construction ) of 50 ohms is specified. | |A 'standard' ground rod is 8 feet long and 1 inch in diameter. | |An average soil resistivity is 500 ohm-metres ( = 2 mS ). See Eznec? | |The calculated resistance of a single standard rod in average soil is 194 |ohms. ( I'm sure the calculating formula can be found somewhere on the IEEE |shelves. There ought to be greater use made of it. ) I responded to this in more detail but the post never came through. So more quickly this time see: http://www.usda.gov/rus/telecom/publ...s/1751f802.pdf [snip] |
#10
![]() |
|||
|
|||
![]()
Roy Lewallen wrote:
Jimmie wrote: Should re read what I write sometimes. I was refering to using the water pipe as the sole ground for your electrical system. This used to be a common thing and pemissable by the NEC, not sure if it still is. When I replaced my service in 1975, a water pipe ground (which is all my 1952 house had) wasn't sufficient to satisfy the NEC, so I had to add a ground rod. So the NEC hasn't permitted a water pipe ground as the sole ground for at least 29 years. It apparently was permissible in 1952. Roy Lewallen, W7EL And I had a friend, had home in Springfield Or., was built during the WAR! Home was plummed with (If you can believe this) Electrical Conduit! Apparently, because of the shortage of materials, this met code then! Stuff finally rotted out, around 1971-- remember him useing his vacation to replum the house! And I had one , in K.Falls, OR was built as old farm house, with steel pipe, that started leaking- electrolysis was rapidly eating it- replaced with Copper. Was curious about the UNIONS used on it-- turns out that those are INSULATED JOINTS! Plumber said had Copper pipes eating out in as little as 3-5 years, before they were available, with them expected 25-30 years, before the pipe gives out! As running current thru a pipe with an insulated connection is worthless as a ground, and even current flowing thru a copper pipe, is hazardious to its health, don't think would recommend this tactic if you want a good ground. Jim NN7K |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
CD Player Receives FM Station | Antenna | |||
Newbie - Studying for Tech & planning station setup - Vertical antennaquestion | Antenna | |||
Antenna mast grounding question | Antenna | |||
Grounding for Vertical Question | Antenna | |||
Grounding question - this is wierd..... | Antenna |