On Mon, 23 Jan 2006 10:25:26 -0800, Richard Clark
wrote: On Mon, 23 Jan 2006 07:29:11 GMT, Owen Duffy wrote: I created a graph to add to an existing web page from the functions for 3mm (bare) wires buried 0.1m Hi Owen, Does this discount the proximity of the radials nearest the center? That is, the graph is not simply a summation of the individual lengths, is it? Richard, See my response to Reg. The functions are from the reference paper you identified. I don't recall that they explained the derivation of the functions, and they may even be fits to experimental data. They do not appear to do something as crude as summing the individual lengths. What would nominal be (in other words, actual) for this specific description above? Did you mean "normalised"? You need to multiply the %/m value from the Y axis by the actual soil resistivity in ohm-metres to get the resistance of the electrode. For example, if you look the chart up for 3 radials of 5m length, you get 15%, which is multiplied by soil resistivity (say 50 ohm-metres at a location) to get expected electrode system "DC/AC" resistance of 7.5 ohms. (The graph is part of a larger article which explains my "normalisation".) Interestingly, I note the ref doc recommends galvanised electrodes. I have been conducting an experiment here where I have recorded the resistance of several driven earth electrodes over some years, and a galvanised electrode of 25mm OD performs much worse than a copper clad electrode of 13mm OD driven just 300mm away from it (both 2.4m long). (The galvanised electrode is not electrically bonded to the earth system for reasons of galvanic corrosion). Owen -- |
#2
|
|||
|
|||
HF-Ground
On Mon, 23 Jan 2006 20:54:19 GMT, Owen Duffy wrote:
Interestingly, I note the ref doc recommends galvanised electrodes. I have been conducting an experiment here where I have recorded the resistance of several driven earth electrodes over some years, and a galvanised electrode of 25mm OD performs much worse than a copper clad electrode of 13mm OD driven just 300mm away from it (both 2.4m long). (The galvanised electrode is not electrically bonded to the earth system for reasons of galvanic corrosion). Hi Owen, What method did you use to measure the resistance? 73's Richard Clark, KB7QHC |
#3
|
|||
|
|||
HF-Ground
On Mon, 23 Jan 2006 13:42:41 -0800, Richard Clark
wrote: On Mon, 23 Jan 2006 20:54:19 GMT, Owen Duffy wrote: Interestingly, I note the ref doc recommends galvanised electrodes. I have been conducting an experiment here where I have recorded the resistance of several driven earth electrodes over some years, and a galvanised electrode of 25mm OD performs much worse than a copper clad electrode of 13mm OD driven just 300mm away from it (both 2.4m long). (The galvanised electrode is not electrically bonded to the earth system for reasons of galvanic corrosion). Hi Owen, What method did you use to measure the resistance? I used a Kyoritsu instrument designed for the purpose. It uses the three wire fall of potential method, and makes its measurements using an AC waveform of about 800Hz. Owen -- |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|