Roy Lewallen wrote:
No, the GFCI doesn't need the safety ground. Like the device you're
describing, it measures the difference between the "hot" and "neutral"
wires, by running the pair together through a transformer. A GFCI is
supposed to trip in 1/40 of a second at 5 mA.

In our system, like yours, the "hot" and "neutral" wires should always
carry equal currents, and the safety ground shouldn't carry any.
However, the safety ground is sized the same as the current-carrying
conductors so it'll handle a fault current large enough to kick the
circuit breaker.


That is pretty much the same as our RCDs, right down to the large-sized
'protective earth' wire.

Its primary function is to protect against something like the "hot"
wire making contact with a metal appliance frame, which should be
connected to the safety ground.


An interesting thing happens when you switch off to isolate part of the
house wiring, and then cut the "dead" three-wire cable. (We call it
"flat twin and earth". It has PVC-insulated hot and neutral wires with a
bare ground wire in between, all in a flattish grey or white PVC sheath.
Is this what you call "Romex"?) If you cut the hot and ground wires
together, nothing happens; but if you cut the neutral and ground wires
together, the RCD trips. That's a puzzle the first time it happens, but
it's because that cable isn't quite as "dead" as you think. the
isolating switches interrupt only the hot wire, so the neutral and earth
are still being shared with everything else that's switched on in the
house.

Does that happen in the USA, or do you have two-pole isolating switches
for individual sub-circuits?

This isn't totally idle curiosity. If there's an electrical problem
while we're staying with the in-laws in Atlanta, I'm the one who's
supposed to know about these things...

When it comes to a GFCI, no assumption is made about how much of the
imbalance current is returned via the safety ground and how much via
the Earth or some other path.

Exactly the same as our RCD, then... just a slightly ambiguous name.


--
73 from Ian G3SEK 'In Practice' columnist for RadCom (RSGB)
Editor, 'The VHF/UHF DX Book'
http://www.ifwtech.co.uk/g3sek
  #2   Report Post  
Old August 9th 03, 10:29 PM
Roy Lewallen
 
Posts: n/a
Default

Ian White, G3SEK wrote:

. . .


An interesting thing happens when you switch off to isolate part of the
house wiring, and then cut the "dead" three-wire cable. (We call it
"flat twin and earth". It has PVC-insulated hot and neutral wires with a
bare ground wire in between, all in a flattish grey or white PVC sheath.
Is this what you call "Romex"?)


Yes, that's "Romex". The official designation is type NM (for
Non-Metallic). 12 gauge wire, for 20 amps maximum, is "12-2 with ground"
and 14 gauge, for 15 amps, is "14-2 with ground". Those are the most
common sizes for residential lighting and outlet circuits.

If you cut the hot and ground wires
together, nothing happens; but if you cut the neutral and ground wires
together, the RCD trips. That's a puzzle the first time it happens, but
it's because that cable isn't quite as "dead" as you think. the
isolating switches interrupt only the hot wire, so the neutral and earth
are still being shared with everything else that's switched on in the
house.

Does that happen in the USA, or do you have two-pole isolating switches
for individual sub-circuits?


I don't quite follow where you're cutting the wires or where the RCD is
located. Here, you can get a GFCI as either a circuit breaker you
install in the service box to protect a whole circuit, or incorporated
in a duplex outlet. Both are easily identifiable by the conspicuous test
button. The breaker differs from an ordinary breaker in that the neutral
wire is also routed through it.

Circuit breakers interrupt only the "hot" wire. It's been a long time
since I studied the code (NEC - National Electrical Code), but I'm sure
that switching the neutral is still a no-no. Neutral wires are all
brought back to the service box, where they're all connected to the
central power feed wire. The safety grounds are brought back to the
service box separately, where they're connected to the same point as the
neutrals. Neutral and safety ground are connected together only at the
service box, nowhere else.

This isn't totally idle curiosity. If there's an electrical problem
while we're staying with the in-laws in Atlanta, I'm the one who's
supposed to know about these things...


I'd at least get a home-handyman book on electrical wiring, and a real
code book if you'll be doing anything other than pretty simple wiring.
The rules are quite complex, dictating things like how close to a
junction box wires have to be supported, how they can be routed, what
size junction box is required for various combinations of
entering/exiting wires, etc. In Oregon, wiring can legally be done only
by the homeowner or a licensed electrician, but each state and many
localities have their own rules. I think all, or just about all, the
states now at least have agreed to use the NEC. (You're probably
technically forbidden to touch the wiring, depending on Georgia and
Atlanta regulations.) The presence of non-code wiring could result in
non-payment of insurance if a home were to have an electrical fire.

I wired the addition to our home, which involved adding seven circuits
including outside outlets and lights. I also replaced and upgraded the
service box. Those jobs were done with electrical work permits, and both
were inspected and passed. So I have done a bit of this before. But it
was a lot of years ago now, the code evolves, and my memory fades.

Roy Lewallen, W7EL

  #3   Report Post  
Old August 9th 03, 10:29 PM
Roy Lewallen
 
Posts: n/a
Default

Ian White, G3SEK wrote:

. . .


An interesting thing happens when you switch off to isolate part of the
house wiring, and then cut the "dead" three-wire cable. (We call it
"flat twin and earth". It has PVC-insulated hot and neutral wires with a
bare ground wire in between, all in a flattish grey or white PVC sheath.
Is this what you call "Romex"?)


Yes, that's "Romex". The official designation is type NM (for
Non-Metallic). 12 gauge wire, for 20 amps maximum, is "12-2 with ground"
and 14 gauge, for 15 amps, is "14-2 with ground". Those are the most
common sizes for residential lighting and outlet circuits.

If you cut the hot and ground wires
together, nothing happens; but if you cut the neutral and ground wires
together, the RCD trips. That's a puzzle the first time it happens, but
it's because that cable isn't quite as "dead" as you think. the
isolating switches interrupt only the hot wire, so the neutral and earth
are still being shared with everything else that's switched on in the
house.

Does that happen in the USA, or do you have two-pole isolating switches
for individual sub-circuits?


I don't quite follow where you're cutting the wires or where the RCD is
located. Here, you can get a GFCI as either a circuit breaker you
install in the service box to protect a whole circuit, or incorporated
in a duplex outlet. Both are easily identifiable by the conspicuous test
button. The breaker differs from an ordinary breaker in that the neutral
wire is also routed through it.

Circuit breakers interrupt only the "hot" wire. It's been a long time
since I studied the code (NEC - National Electrical Code), but I'm sure
that switching the neutral is still a no-no. Neutral wires are all
brought back to the service box, where they're all connected to the
central power feed wire. The safety grounds are brought back to the
service box separately, where they're connected to the same point as the
neutrals. Neutral and safety ground are connected together only at the
service box, nowhere else.

This isn't totally idle curiosity. If there's an electrical problem
while we're staying with the in-laws in Atlanta, I'm the one who's
supposed to know about these things...


I'd at least get a home-handyman book on electrical wiring, and a real
code book if you'll be doing anything other than pretty simple wiring.
The rules are quite complex, dictating things like how close to a
junction box wires have to be supported, how they can be routed, what
size junction box is required for various combinations of
entering/exiting wires, etc. In Oregon, wiring can legally be done only
by the homeowner or a licensed electrician, but each state and many
localities have their own rules. I think all, or just about all, the
states now at least have agreed to use the NEC. (You're probably
technically forbidden to touch the wiring, depending on Georgia and
Atlanta regulations.) The presence of non-code wiring could result in
non-payment of insurance if a home were to have an electrical fire.

I wired the addition to our home, which involved adding seven circuits
including outside outlets and lights. I also replaced and upgraded the
service box. Those jobs were done with electrical work permits, and both
were inspected and passed. So I have done a bit of this before. But it
was a lot of years ago now, the code evolves, and my memory fades.

Roy Lewallen, W7EL

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you recognize yourself ? Stef Antenna 3 January 5th 04 06:16 PM
WTB: Brass "Signal Electric" key Michael White Boatanchors 0 September 21st 03 03:35 PM
WTB: Brass "Signal Electric" key Michael White Boatanchors 0 September 21st 03 03:35 PM
102-E Western Electric Tube info needed Jim Rayburn Boatanchors 0 August 20th 03 05:15 PM
FA: Pair Western Electric 106F Speakers! 6-Hrs..Left! MTM Boatanchors 0 August 5th 03 05:29 PM


All times are GMT +1. The time now is 08:40 PM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 RadioBanter.
The comments are property of their posters.
 

About Us

"It's about Radio"

 

Copyright © 2017